[技术互助] A Tip on changing 3 phase AC motor rotation

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
本帖最后由 td456 于 2010-4-14 12:28 编辑
5 N# N$ @, S1 V( B
" s" o9 Y2 Q- h3 AWe all know that if you want to change the rotation of a three  phase AC motor.( d: L" d& r& p
Just swap any of the two phase leads./ X" \4 L9 c  B7 m! J3 n; A+ |
But for VFD application you need to do the swap after the inverter./ p7 u% }. C" ?. R1 l8 F2 T
If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
8 q; j2 t" W% M' T; K# |% D$ }
- i+ ]/ v$ D% o0 H6 gAs the principal of the VFD works, bascially from AC to DC, then DC to AC.
  P3 O, Y8 `9 Y. k8 R8 x1 E; Q1 t2 B9 y% _+ z/ f) a6 r! r5 K
The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.! F8 m" t& R5 f4 D# w

' w+ M- b3 a  }. I1 t+ ^The only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.