[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-4-14 12:28 编辑 ) l  k: I' E6 u2 E/ s( i6 O, V

' F0 e+ h) S1 [( o: A+ x. Q/ P$ x: S7 wWe all know that if you want to change the rotation of a three  phase AC motor.+ [- M5 n; u0 A3 O3 K$ ?" @3 v
Just swap any of the two phase leads.
# A8 g8 l8 q3 l: r# Q8 d) @But for VFD application you need to do the swap after the inverter.  S9 d3 |  o7 u1 P7 J! ^
If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.# J$ m9 j' U- l6 i% X& [& p" I
  f$ F/ Q, _3 d
As the principal of the VFD works, bascially from AC to DC, then DC to AC. 1 |3 X# J1 r5 a4 h8 A& G

( Q- U4 K- c0 q0 R& f, K9 v/ yThe phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.
- A% i6 ^, M! _0 r
; b$ \  D7 s* o# l$ lThe only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.