, D$ l/ d& o! L8 mTwo cutler –hammer advantage starters are doing the same thing:; v" `5 b/ }4 k% h& l! F) B/ {
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again. 4 ]/ M' A2 D/ l3 W" p2 p
It is a cycle./ Q! ]& t( ~7 G0 e
+ O. t& N5 F( I, t, ?1 { B% ]We isolate the network control and use the local start and stop only, the problem remains.
: |& p$ A" x$ W% e3 J, ASwap one of the defective buckets with a good one, the new bucket works fine.
5 O7 F# C% ^& @. l' M8 WThe problem should be inside the bucket.
9 O2 R5 K6 ~0 Y( C v5 z3 T3 o" M1 S8 P% @& N
When the problem happened, we observed that the contactor has a pulling action but will not seal.. z9 @) m7 s& l' Q! v
Use a terminating screw divers to push in the contactor, it will not seal either." A3 e V# r! f& B G3 P
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
& a2 z, z8 B b4 L4 P Z" B6 b7 E; ? v6 X9 o" ^% W+ _
The next thing we can think of is the coil, we took the coil out to have a close look.
! }+ v- H5 O+ L. y9 m0 o! OThey have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.0 T( S" D' a+ Y: K. I: b
It is getting better this time, we have 7-8 times of running before it quit working. / n8 x Q0 ]: L% f/ G
9 k+ a3 M; F% i: o! ~/ SThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
9 t0 H, c, m1 m0 C" b1 m/ t G# ?0 ?* a
Do you guys have any input on this issue? |
|