Two cutler –hammer advantage starters are doing the same thing:
! `9 M" a z9 h. V' @. C" z After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again. + I8 ~) f; P: T+ P
It is a cycle.
+ K+ V2 e8 ?3 M% Q$ J* a% J9 M; _. |1 S! ?
We isolate the network control and use the local start and stop only, the problem remains., \' P/ Q# L& v$ Q
Swap one of the defective buckets with a good one, the new bucket works fine.
1 S' ?1 \& \; [7 y+ qThe problem should be inside the bucket.
9 \( \4 _- F M7 s; l6 e) x" G7 ~ K3 x$ m" e% X
When the problem happened, we observed that the contactor has a pulling action but will not seal.; n$ `0 U5 I% z2 z/ P# [
Use a terminating screw divers to push in the contactor, it will not seal either.
# y4 i" N+ g! X- WConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
" C! s5 {8 [4 c1 e3 z: Z e8 i" C4 i% h! e$ Q- y2 x
The next thing we can think of is the coil, we took the coil out to have a close look.: ~" L: U' S; `" ]
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again. K- N% U3 u/ o( M
It is getting better this time, we have 7-8 times of running before it quit working. 2 @/ g6 y# Q* `% @$ O0 V( [( I
, y4 `1 I7 a3 o) q# h# w+ `' ]
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
) [! O \) ^/ {7 W' r% U. p6 B' \6 l' c; U& m t/ ~ w! P$ ^5 Y
Do you guys have any input on this issue? |
|