Two  cutler –hammer advantage  starters are  doing the same thing:, t5 v3 s: ]% W+ }2 e9 [( |5 N* M, X
After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again. ) X1 q5 |. l% H0 h% I4 r8 N
It is a cycle.
2 z; d( s6 R9 B. ^* ~$ K
) t/ s! ]) y# s' f" ]. tWe isolate the network control and use the local start and stop only, the problem remains.
3 n4 j9 z3 s- }Swap one of the defective buckets with a good one, the new bucket works fine.
' ^; u9 n- `6 ~( o+ XThe problem should be inside the bucket.' m$ S% J9 ~8 c% X
! p9 Q1 X' w& S! E/ K
When the problem happened, we observed that  the contactor has a pulling action but will not seal.& Y/ n' k) }* b( y/ \% l5 K: O
Use a terminating screw divers to push in the contactor, it will not seal either.: T; K7 C! |% ~: \# ]/ f
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.
( V9 F; C  F5 [7 K+ Q0 T) C9 ~: j0 _0 ~7 m# Q: b
The next thing we can think of  is the coil, we took the coil out to have a close look.: x' E2 Y) l3 F- _1 |$ G
They  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.
* G' ^; G9 }& O, [3 p6 S4 r It is getting better  this time, we have 7-8 times of running before it quit working.
; [7 `- k4 E0 \9 A( P4 O# a
9 A$ M) o3 Q' o. E0 `The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
8 g. W6 {0 X# `# }  F4 ?" G3 ~' _1 G3 n# B$ d
Do you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑
3 Z+ c2 I% y# w
3 ]& X. X! ?8 O中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.3 g/ Z# c6 W6 L
Since your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行 3 V. r. [: E2 _8 W- d
也想到这一点,不过这是新装的设备。
# D( K% M, T5 @' ^- F检查过触点没问题。