Two cutler –hammer advantage starters are doing the same thing:' i) z2 T0 Z7 g7 J, ]- v
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again. : r; H4 g/ d N9 \% X
It is a cycle.! G* @9 z$ Y9 g: s# M' {4 t
2 Q6 ^6 T) i+ x. z2 A6 [. Y0 UWe isolate the network control and use the local start and stop only, the problem remains.
' K8 F1 F. w9 ?$ r3 c0 n4 ^1 ISwap one of the defective buckets with a good one, the new bucket works fine.
6 N& b# }( N7 o: [& j; v2 QThe problem should be inside the bucket.
2 ~5 _5 W' w' h6 m1 W/ b! E, D! m: i4 u6 s4 P
When the problem happened, we observed that the contactor has a pulling action but will not seal.
5 d8 ~2 M o% X# fUse a terminating screw divers to push in the contactor, it will not seal either.0 q, F$ m7 L- G$ _ F: C
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
8 T, _3 r* `/ A/ U$ R0 L6 V, b5 K0 q' g: Y7 C( p# g4 u
The next thing we can think of is the coil, we took the coil out to have a close look.
" S- |. m$ Q: G$ Q; {, |They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.
& d2 u8 s$ X; d, p, p1 @ It is getting better this time, we have 7-8 times of running before it quit working. - {7 V7 s D4 H. g- M& `
. S, q9 y8 j/ l! X& BThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. 3 a% Q/ K, u) w
|; U( r) ]- P9 G. E: t2 C1 S
Do you guys have any input on this issue? |
|