Two cutler –hammer advantage starters are doing the same thing:! s$ G/ ?* s( c! H w: ]9 o2 ?
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again. , l" r" ~3 M( t( P) s
It is a cycle.
8 k5 ?1 F+ a+ h4 h: {; W( w8 j# e) p# \# |( Y
We isolate the network control and use the local start and stop only, the problem remains.
5 } d+ n* @0 H- x! vSwap one of the defective buckets with a good one, the new bucket works fine.
" H( o0 m; H0 MThe problem should be inside the bucket.: s% ]* I5 k' I) u8 ^. C
9 h& h p; ` M* r6 X2 BWhen the problem happened, we observed that the contactor has a pulling action but will not seal.
$ V9 a# n8 I2 }. M2 b# }( KUse a terminating screw divers to push in the contactor, it will not seal either.; A% H9 l/ i6 d- k9 M0 f
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
, z5 d4 v! z( Q9 g0 ], q3 s- ^5 Q: m% @' l9 A
The next thing we can think of is the coil, we took the coil out to have a close look.* T/ O% }4 S7 `) M9 l1 M0 d
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.
" ^8 U2 U9 U9 B7 j) @, }2 `" Y It is getting better this time, we have 7-8 times of running before it quit working. 5 Y2 K5 E0 t/ k! M5 `% J1 }8 u
: z" U0 F. X: T; m4 J2 U% J
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
0 X% g. w6 v8 Y/ X6 B3 m- i4 ^. E# ^2 p+ @
Do you guys have any input on this issue? |
|