[技术互助] A Tip on changing 3 phase AC motor rotation

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-4-14 12:28 编辑
+ {- n1 b8 s' n+ n7 Q9 W- z
* l% v+ I3 }# H& A( M7 }; c) l# aWe all know that if you want to change the rotation of a three  phase AC motor.0 I( I( d  _; }, x
Just swap any of the two phase leads.
, a0 q7 O( p$ i, OBut for VFD application you need to do the swap after the inverter.
6 z: w. {% k5 `+ k/ cIf you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.; `+ G7 U" m! L# L* x+ O: A+ Z

. B6 ~# t; Y; ~0 {! J  M+ kAs the principal of the VFD works, bascially from AC to DC, then DC to AC.
0 M3 n1 M0 A2 h1 r2 a# S- P
$ B/ x2 I$ }: f1 f6 w! I% M0 {5 V# GThe phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.
7 m$ n/ m3 X' l4 F  Z0 R8 Z9 f: z+ c* r5 H9 s# ]
The only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.