[技术互助] A Tip on changing 3 phase AC motor rotation

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-4-14 12:28 编辑
% v1 R, T1 M3 X2 M1 z% I: [  c3 i. L
We all know that if you want to change the rotation of a three  phase AC motor.3 I: ]( B# K- i3 B& b. g& p
Just swap any of the two phase leads.
- ?! V, @0 V* O: @2 oBut for VFD application you need to do the swap after the inverter.
5 B  ]  L( w+ b* S( U& D8 [If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
% h$ x- j- ^5 I6 F: c8 [' j1 r- i$ y6 K7 R% k& R
As the principal of the VFD works, bascially from AC to DC, then DC to AC.
  E0 T% e" r4 F( w: ~  l7 |8 E6 u
The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.6 H; g5 D0 k5 ?# p: B

5 Y# {: M1 R6 VThe only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.